    I have a friend, with a 5 HP submersible pump. Single phase 230. Overheating a 40 amp circuit breaker. Put an ampmeter on it, 25 amps one leg 27 amps the other leg. Circuit breaker itself was too hot to touch, wires weren't hot. We replaced the breaker, all seems fine now, not overheating, amp readings are 25 amps both sides.

    Question: What amp readings should I be getting with a properly operating 5 HP submersible? I checked mine, but I have a three phase turbine, not the same thing.

    Thanks,

    Joe
    *** Disclaimer ***

    As I have no wish to toy with anybody's life, I suggest you take this and all other posts with a certain amount of skepticism. Carefully evaluate, and if necessary, research on your own any suggestions or advice you might pick up here, especially those from my posts, as I obviously haven't the skill and experience exhibited by some of the more illustrious and more successful members of this forum. I'm not responsible for anything I say, as I drank toxic water when young.

  • #2
    Considering that one hp = 746 watts, along with losses for motor efficiency and lagging power factor (amps that go to forming the motor's magnetic field but do not do any "real" work), 25 amps sounds reasonable. However, with a single phase, what goes in one leg should come out the other. Barring any measurement error, you should see the same current in each leg. Did you check the ground wire? It should read near zero. I'm wondering if there is some insulation breakdown and leakage current into the ground wire or the well/ground.
    Blacksmith
    Stickmate LX AC/DC
    Big cheap (Chinese) Anvil
    Hand cranked coal forge
    Freon bottle propane forge
    HH 210 and bottle of C25

    Comment


    • #3
      Originally posted by Blacksmith View Post
      Considering that one hp = 746 watts, along with losses for motor efficiency and lagging power factor (amps that go to forming the motor's magnetic field but do not do any "real" work), 25 amps sounds reasonable. However, with a single phase, what goes in one leg should come out the other. Barring any measurement error, you should see the same current in each leg. Did you check the ground wire? It should read near zero. I'm wondering if there is some insulation breakdown and leakage current into the ground wire or the well/ground.
      Once we replaced the breaker, both legs are essentially equal.
      *** Disclaimer ***

      As I have no wish to toy with anybody's life, I suggest you take this and all other posts with a certain amount of skepticism. Carefully evaluate, and if necessary, research on your own any suggestions or advice you might pick up here, especially those from my posts, as I obviously haven't the skill and experience exhibited by some of the more illustrious and more successful members of this forum. I'm not responsible for anything I say, as I drank toxic water when young.

      Comment


      • #4
        Then likely the breaker was bad. They do fail/wear out. I didn't carefully read the original post. But I stand by ~25 amps being correct for 5 hp single phase.
        Blacksmith
        Stickmate LX AC/DC
        Big cheap (Chinese) Anvil
        Hand cranked coal forge
        Freon bottle propane forge
        HH 210 and bottle of C25

        Comment


        • #5
          Thanks. Checked the motor plate on a 5hp commercial compressor (NOT homeowner type), amps were listed as 22. I figured we were in the ballpark. My own pump (three phase) pulls about 15 amps.
          *** Disclaimer ***

          As I have no wish to toy with anybody's life, I suggest you take this and all other posts with a certain amount of skepticism. Carefully evaluate, and if necessary, research on your own any suggestions or advice you might pick up here, especially those from my posts, as I obviously haven't the skill and experience exhibited by some of the more illustrious and more successful members of this forum. I'm not responsible for anything I say, as I drank toxic water when young.

          Comment


          • #6
            Three phase power watts (hp) is volts x amps x 1.73 (square root of 3), so if the single phase 5 hp is drawing 25 per line, 15 per line on 3 phase is in the ballpark.
            Blacksmith
            Stickmate LX AC/DC
            Big cheap (Chinese) Anvil
            Hand cranked coal forge
            Freon bottle propane forge
            HH 210 and bottle of C25

            Comment


            • #7
              I ran into an old friend/ retired electrician who used to own the most professional electrical/pump shop around, he told me 25 amps for a single phase 5 hp pump is well within tolerances. Thanks for your input, Blacksmith, you were correct.
              *** Disclaimer ***

              As I have no wish to toy with anybody's life, I suggest you take this and all other posts with a certain amount of skepticism. Carefully evaluate, and if necessary, research on your own any suggestions or advice you might pick up here, especially those from my posts, as I obviously haven't the skill and experience exhibited by some of the more illustrious and more successful members of this forum. I'm not responsible for anything I say, as I drank toxic water when young.

              Comment


              • #8
                You're more than welcome. I dabble in this stuff at work. New diesel gensets arriving.
                Click image for larger version

Name:	Exit Ramp[1].jpg
Views:	1
Size:	50.8 KB
ID:	665850
                Blacksmith
                Stickmate LX AC/DC
                Big cheap (Chinese) Anvil
                Hand cranked coal forge
                Freon bottle propane forge
                HH 210 and bottle of C25

                Comment

                Working...
                X