  • Running MVP 210 off a generator

    HELP! I need to remotely weld with my MVP 210 off a generator. (Or find a 5 mile extension cord...)I tried 2000 watt, 4000 watt and 6000watt generators with no success. I tried .035, .030 and .024 wire with and without gas with no luck. I tried every heat setting. No luck. I turned off the generator idle control so generator was blasting full speed when I tried to strike the arc. No luck. I tried both 110 and 220v outputs on generators. No luck. All I get is loud hum from the welder and tiny bubble arcs of weld with little/no penetration. When I take the welder back in shop and hook it to building 220v it works fine. Doc you gotta help me here!!

  • #2
    For MPV 210 at top end settings it takes about a 7000 watts (minimum) generator, its recommended that any generator have about 50% more capacity than welder requires so a 10,000 watt unit probably would fit the bill,,,, Suggest you use 240 Volt 30 AMP outlet on generator with proper adapter plug....



    Reason for big generator is the smaller units have small rotating mass of armature and it can not sustain momentum when you strike arc and causes generator to bog down... If generator has "sustained speed" setting suggest you use that instead of letting generator to "idle down"...

    Dale
    Last edited by Dale M.; 02-11-2019, 02:37 PM.
    Lives his life vicariously through his own self.