HH190 breaker sizing

Collapse
X
  • Filter
  • Time
  • Show
Clear All
new posts

  • HH190 breaker sizing

    Hi, new to the forum. Am about to buy a HH190, and want to have what I need on hand to install new 240v run. It shows the "generator size" of like 5660 watts. A quick calculation gives me 5660 watts @ 240v = about 24 amps. So are you 190 users on a 30 amp 240 v breaker?

  • #2
    Welcome to the forum aboutlastnite.
    You should be good to go.
    Lincoln A/C 225
    Everlast PA 200

    Comment


    • #3
      This document on page 16....

      http://www.hobartwelders.com/om/6digit/o260273c_hob.pdf

      States normal input at 20.5 amps and recommends a "normal" fuse at 30 amp.... So yes 30 amp circuit should be sufficient...

      Document also state welder uses NEMA 6-50 plug/receptacle combination....

      Dale
      Lives his life vicariously through his own self.

      Comment


      • #4
        Cool, thanks fellas.

        Comment


        • #5
          It can be used with breakers 30 to 50 provided the wire is 12 or better. They are designed to run on common welder circuits to 50A
          http://www.facebook.com/cary.urka.urkafarms

          Comment


          • #6
            A tailor made circuit for them is a 10/30. They run fine on a 12 but I figure a small machine needs all the help it can get and you can run a buzzer on the same wire with a breaker change if needed.
            http://www.facebook.com/cary.urka.urkafarms

            Comment


            • #7
              190 wireup

              I am using the 10/30 wireup for my handler and its running great. Very happy with the wireup.