    I have 10/3 wire going from my house to the garage about 75 feet away. My hh210 works fine, but I need an esxention to get out of the garage.I have a 30 amp breaker it the house and in the garage. I am thinking that I will have to add the 75' to the extention cord to determine the length of the cord that I can use. How long of a cord can I make?

  • #2
    Thats about the limit.
    http://www.facebook.com/cary.urka.urkafarms

    Comment


    • #3
      Well then, I had better make an extention cord for my Champion.

      Comment


      • #4
        Thanks Sberry. I thought so, but wanted another oopenion. Someone with more sence than me.

        Comment


        • #5
          A little will depend on the incoming voltage as to whats acceptable, that is a total of 150 ft and the 210 runs about 20A or so with 030. I wouldn't want to run much farther than that from a 10 but if this is going to be used much the cord will be worth it, very expensive to run an engine drive for any amount of time doing general fab work. I would want to be plugged in to the wall if I could. The big point of a Champ is stick machine, I use sticks away from the shop, I wouldn't want to fart with moving other equipment unless I absolutely had to.
          http://www.facebook.com/cary.urka.urkafarms

          Comment


          • #6
            I want to make a 12fot trailer and I have a small garage

            I want to make a 12 foot trailor with my new hh210 and I have a small garage that is loaded with equipment. I will have to make it outside. Don't look like I have much choice.

            Comment


            • #7
              Do you think I might get by with a 20 foot cord?

              Comment


              • #8
                sure, even a bit longer will be fine. I was under the impression that you wanted to add another 75 ft.
                http://www.facebook.com/cary.urka.urkafarms

                Comment


                • #9
                  Thanks you made my day.You have given me a whole lot of help lately. I sure appreciate it.

                  Comment


                  • #10
                    I was thinking that the 75 foot from the house to the garage must be added to the extention cord. It would be like using a 90 foot cord.

                    Comment


                    • #11
                      It will be a 90 ft cord essentially but the welder will run fine from that provided there isn't other things running from the same line. With a 10 wire you could be out 125, 150 ft no problem depending of the quality of service.
                      http://www.facebook.com/cary.urka.urkafarms

                      Comment


                      • #12
                        Thanks, everything will be OK

                        Comment


                        • #13
                          Oh, do watch out for the quality of your plugs, receptacles and their connections.